Transform curves extracted from beams
Hi All, @c.poupin
In the main purpose to create beams rebars and in continuation of my previous topic Beams length from outer faces, where I was able to retrieve and extend the max_edge curves from an intersecting beam network using uncut solid geometry, my main goal now is to improve the code and make it cleaner starting by properly setting and getting beam covers, and then applying the necessary transformations to the extracted curves accordingly.
When I run the code, the cover parameters are updated as expected from the input values and correctly displayed in the properties tab for all beams., however unlike top_cover and btm_cover I’m having an issue retrieving the side_cover parameter within curve_multiply_offset function as you can see in the error displayed in the image below and this prevents the required curve transformations from being applied within the main function get_corrected_beam_length.
Please check my attached code and revit file:
Transform curves
import sys
import System
from System.Collections.Generic import IList, List
clr.AddReference('RevitAPI')
clr.AddReference("System.Core")
clr.ImportExtensions(System.Linq)
rebar_types = (FilteredElementCollector(doc)
        .OfCategory(BuiltInCategory.OST_Rebar)
        .WhereElementIsElementType()
        .WherePasses(ElementClassFilter(RebarBarType))
        .ToElements())
top_bar_type = next((r for r in rebar_types if r.LookupParameter('Diamètre de barre').AsValueString() == "12 mm"), None)
btm_bar_type = next((r for r in rebar_types if r.LookupParameter('Diamètre de barre').AsValueString() == "14 mm"), None)
stirrup_type = next((r for r in rebar_types if r.LookupParameter('Diamètre de barre').AsValueString() == "6 mm"), None)
hook_types = list(FilteredElementCollector(doc)
                  .OfClass(RebarHookType)
                  .ToElements())
stirrup_hook_types = [hk for hk in hook_types if hk.Style == RebarStyle.StirrupTie]
standard_hook_types = [hk for hk in hook_types if hk.Style == RebarStyle.Standard]
hook_90 = next((h for h in standard_hook_types if Element.Name.GetValue(h) == "Standard - 90 deg."), None)
hook_135 = next((h for h in stirrup_hook_types if Element.Name.GetValue(h) == "Etrier/épingle - 135 deg."), None)
cover_faces = {
    "Top": BuiltInParameter.CLEAR_COVER_TOP,
    "Bottom": BuiltInParameter.CLEAR_COVER_BOTTOM,
    "Other": BuiltInParameter.CLEAR_COVER_OTHER
cover_types = list(FilteredElementCollector(doc).OfClass(RebarCoverType).ToElements())
def get_cover_type(distance):
    for ct in cover_types:
        if abs(ct.CoverDistance - distance) < 1e-6:
            return ct
    name = "Enrobage_{} cm".format(distance / 0.0328084)
    new_ct = RebarCoverType.Create(doc, name, distance)
    cover_types.append(new_ct)
    return new_ct
def set_beam_covers(beam, top, btm, side):
    cover_cm = {"Top": top, "Bottom": btm, "Other": side}
    cover_ft = {face: cover_cm[face] * 0.0328084 for face in cover_cm}
    for face, bip in cover_faces.items():
        param = beam.get_Parameter(bip)
        if param and param.StorageType == StorageType.ElementId:
            ct = get_cover_type(cover_ft[face])
            if ct:
                param.Set(ct.Id)
def get_beam_covers(beam):
    result = {}
            ct = doc.GetElement(param.AsElementId())
            if isinstance(ct, RebarCoverType):
                result[face] = ct.CoverDistance
    return result
def get_solid(beam):
    options = Options()
    options.IncludeNonVisibleObjects = False
    options.DetailLevel = ViewDetailLevel.Fine
    geoElement = beam.get_Geometry(options)
    return next((g for g in geoElement if isinstance(g, Solid) and g.Volume > 0), None)
def get_side_face_normal(solid, edge):
    for face in solid.Faces:
        if edge in [e for loop in face.EdgeLoops for e in loop]:
            normal = face.FaceNormal
            if not (normal.IsAlmostEqualTo(XYZ.BasisZ) or normal.IsAlmostEqualTo(-XYZ.BasisZ)):
                return normal
    return None
def is_curves_parallel(curve1, curve2, tolerance=1e-6):
    vect1 = curve1.Direction.Normalize()
    vect2 = curve2.Direction.Normalize()
    return vect1.CrossProduct(vect2).GetLength() <= tolerance
def curve_multiply_offset(curve, vector, distance, top_cover, btm_cover, side_cover):
    curve = curve.CreateTransformed(Transform.CreateTranslation(XYZ(0, 0, -1).Multiply(top_cover)))
    vertical_offset = distance - (top_cover + btm_cover)
    trans = Transform.CreateTranslation(vector.Negate().Multiply(side_cover))
    top_curve = curve.CreateTransformed(trans)
    bottom_trans = Transform.CreateTranslation(XYZ(0, 0, -1).Multiply(vertical_offset))
    btm_curve = top_curve.CreateTransformed(bottom_trans)
    btm_curve = Line.CreateBound(btm_curve.GetEndPoint(1), btm_curve.GetEndPoint(0))
    return top_curve, btm_curve
def get_intersecting_end_beams_data(single_beam, all_beams, tolerance=0.001):
    loc_curve = single_beam.Location.Curve
    w = single_beam.Symbol.LookupParameter("b").AsDouble()
    h = single_beam.Symbol.LookupParameter("h").AsDouble()
    single_beam_covers = get_beam_covers(single_beam)
    top_cover = single_beam_covers.get("Top")
    btm_cover = single_beam_covers.get("Bottom")
    side_cover = single_beam_covers.get("Other")
    start = loc_curve.GetEndPoint(0)
    end = loc_curve.GetEndPoint(1)
    w_start = None
    w_end = None
    start_side_cover = 0
    end_side_cover = 0
    for beam in all_beams:
        if beam.Id == single_beam.Id:
            continue
        other_curve = beam.Location.Curve
        b = beam.Symbol.LookupParameter("b").AsDouble()
        other_beam_covers = get_beam_covers(beam)
        other_side_cover = other_beam_covers.get("Other")
        if is_curves_parallel(loc_curve, other_curve):
            continue
        projected_start = other_curve.Project(start)
        if projected_start and projected_start.Distance < tolerance and w_start is None:
            w_start = b / 2
            start_side_cover = other_side_cover
            print(start_side_cover * 0.3048)
        projected_end = other_curve.Project(end)
        if projected_end and projected_end.Distance < tolerance and w_end is None:
            w_end = b / 2
            end_side_cover = other_side_cover
            print(end_side_cover * 0.3048)
    return {
        "beam_width": w,
        "beam_height": h,
        "beam_top_cover": top_cover,
        "beam_btm_cover": btm_cover,
        "beam_side_cover": side_cover,
        "width_start": w_start,
        "width_end": w_end,
        "beam_start_side_cover": start_side_cover,
        "beam_end_side_cover": end_side_cover
def get_corrected_beam_length(beam, all_beams):
    beam_curve = beam.Location.Curve
    direction = beam_curve.Direction
    beam_length = beam_curve.Length
    start = beam_curve.GetEndPoint(0)
    cut_elems = [doc.GetElement(xId) for xId in SolidSolidCutUtils.GetCuttingSolids(beam)]
    for e in cut_elems:
        JoinGeometryUtils.SwitchJoinOrder(doc, beam, e)
    doc.Regenerate()
    solid = get_solid(beam)
    if not solid:
        return None
    max_edge = max(solid.Edges, key=lambda x: x.ApproximateLength)
    max_edge_curve = max_edge.AsCurve()
    max_edge_direction = max_edge_curve.Direction
    max_edge_length = max_edge_curve.Length
    face_normal = get_side_face_normal(solid, max_edge)
    if face_normal is None:
        return None
    intersection_data = get_intersecting_end_beams_data(beam, all_beams)
    beam_width = intersection_data["beam_width"]
    beam_height = intersection_data["beam_height"]
    top_cover = intersection_data["beam_top_cover"]
    btm_cover = intersection_data["beam_btm_cover"]
    side_cover = intersection_data["beam_side_cover"]
    w_start = intersection_data["width_start"] or 0
    w_end = intersection_data["width_end"] or 0
    start_side_cover = intersection_data["beam_start_side_cover"]
    end_side_cover = intersection_data["beam_end_side_cover"]
    if max_edge_length > beam_length:
        if not max_edge_curve.GetEndPoint(0).Z == beam_curve.GetEndPoint(0).Z:
            max_edge_curve = Line.CreateBound(XYZ(max_edge_curve.GetEndPoint(0).X, max_edge_curve.GetEndPoint(0).Y, beam_curve.GetEndPoint(0).Z), XYZ(max_edge_curve.GetEndPoint(1).X, max_edge_curve.GetEndPoint(1).Y, beam_curve.GetEndPoint(1).Z))
        if not max_edge_direction.IsAlmostEqualTo(direction):
            max_edge_curve = Line.CreateBound(max_edge_curve.GetEndPoint(1), max_edge_curve.GetEndPoint(0))
        new_start = max_edge_curve.Evaluate(start_side_cover / max_edge_length, True)
        new_end = max_edge_curve.Evaluate(1 - (end_side_cover / max_edge_length), True)
        new_line = Line.CreateBound(new_start, new_end)
        total_length = beam_length + w_start + w_end - (start_side_cover + end_side_cover)
        project_point = start + face_normal.Multiply(beam_width / 2)
        new_start = project_point - direction.Multiply(w_start - start_side_cover)
        new_end = new_start + direction.Multiply(total_length)
    top_curve, btm_curve = curve_multiply_offset(new_line, face_normal, beam_height, top_cover, btm_cover, side_cover)
    return btm_curve, top_curve, face_normal
def split_curve(curve, bartype):
    total_length = curve.Length
    unit_length = 12.0 / 0.3048
    diameter = bartype.BarModelDiameter
    lr = 50 * diameter
    min_remainder = 2.0 / 0.3048
    tol_near_full = 0.2 / 0.3048
    direction = curve.Direction
    curves = []
    start = curve.GetEndPoint(0)
    k = 0
    n = int(total_length // unit_length)
    if total_length <= unit_length:
        curves.append(curve)
        while k < n:
            end = start.Add(direction.Multiply(unit_length))
            new_line = Line.CreateBound(start, end)
            curves.append(new_line)
            k += 1
            next_start = start.Add(direction.Multiply(unit_length - lr))
            remaining_length = curve.GetEndPoint(1).DistanceTo(end)
            if remaining_length < unit_length - lr:
                remainder_end = curve.GetEndPoint(1)
                if remaining_length <= lr or remaining_length < min_remainder:
                    adjusted_start = remainder_end.Add(direction.Multiply(min_remainder).Negate())
                    remainder_line = Line.CreateBound(adjusted_start, remainder_end)
                    remainder_line = Line.CreateBound(next_start, remainder_end)
                    if remainder_line.Length < (unit_length - tol_near_full):
                        remainder_line = remainder_line
                        adjusted_start = remainder_end.Add(direction.Multiply(unit_length).Negate())
                curves.append(remainder_line)
                break
            start = next_start
    return curves
beams = FilteredElementCollector(doc)\
    .OfCategory(BuiltInCategory.OST_StructuralFraming)\
    .WhereElementIsNotElementType()\
    .Where(System.Func[DB.Element, System.Boolean](lambda b : b.StructuralUsage == StructuralInstanceUsage.Girder))\
    .ToList()
with Transaction(doc, "Set beams Covers") as t:
    t.Start()
    for b in beams:
        set_beam_covers(b, 10, 15, 8)
    t.Commit()
btm_curves = []
top_curves = []
with Transaction(doc, "split rebars") as t:
    t.Start()
    for beam in beams:
        direction = beam.Location.Curve.Direction
        width = beam.Symbol.LookupParameter("b").AsDouble()
        result = get_corrected_beam_length(beam, beams)
        if not result:
            continue
        btm_curve, top_curve, normal_vect = result
        bc = split_curve(btm_curve, btm_bar_type)
        tc = split_curve(top_curve, top_bar_type)
        btm_curves.append(bc)
        top_curves.append(tc)
    t.Commit()
OUT = [c.ToProtoType() for lst in btm_curves for c in lst], [c.ToProtoType() for lst in top_curves for c in lst]
beams_network1.rvt (1.9 MB)
Any help to solve this issue would be greatly appreciated.
Thanks.
I don’t have the same error. Rather than providing the complete code, try providing the part of the code that is causing the problem.
@c.poupin
here the edited code without split_curve function
import sys
import System
# cover parameters by faces
cover_faces = {
            return ct
    return new_ct
            if ct:
                param.Set(ct.Id)
    result = {}
    return result
    options = Options()
                return normal
    return None
    w_start = None
    w_end = None
    end_side_cover = 0
            continue
            continue
            w_start = b / 2
            w_end = b / 2
    return {
        "beam_width": w,
        "beam_height": h,
        "width_end": w_end,
    for e in cut_elems:
    doc.Regenerate()
    if not solid:
        return None
        return None
# Collect beams
    .ToList()
    t.Start()
    for b in beams:
    t.Commit()
btm_curves = []
top_curves = []
    t.Start()
    for beam in beams:
        if not result:
            continue
        btm_curves.append(btm_curve)
        top_curves.append(top_curve)
    t.Commit()
OUT = [c.ToProtoType() for c in btm_curves], [c.ToProtoType() for c in top_curves]
Thanks.
There are six built in parameters that relate to rebar cover - it’s quite possible that the ‘other’ value is None.
CLEAR_COVER       “Rebar Cover”
CLEAR_COVER_BOTTOM   “Rebar Cover - Bottom Face”
CLEAR_COVER_TOP      “Rebar Cover - Top Face”
CLEAR_COVER_OTHER    “Rebar Cover - Other Faces”
CLEAR_COVER_INTERIOR  “Rebar Cover - Interior Face”
CLEAR_COVER_EXTERIOR “Rebar Cover - Exterior Face”
Hi @Mike.Buttery
I’m sorry for the delayed feedback …I was traveling and couldn’t respond earlier!
I’m not sure how to access all those parameters. The beams I collected only include the cover parameters I’m currently working with..the ones visible under the Properties tab. I also found them using Revit Lookup, as you can see in the image below:
I also found this topic on the Revit API forum discussing rebar cover parameters. It uses the same built-in parameters I’m currently accessing to update cover values, so I’m not sure when or why the other parameters you mentioned would be used.
Thanks.
Beams do use the three cover parameters in your code, so not adjustment required - therefore some of the parameters appear to not have a value. You could add a LogicalAndFilter to your beam collector to ensure all elements have the parameters you require.
Example code:
clr.AddReference("RevitAPI")
def logical_and_filter(bips):
    pfrs = [
        ParameterFilterRuleFactory.CreateHasValueParameterRule(ElementId(bip))
        for bip in bips
    return LogicalAndFilter([ElementParameterFilter(pfr) for pfr in pfrs])
laf = logical_and_filter(
        BuiltInParameter.CLEAR_COVER_OTHER,
OUT = (
    .WherePasses(laf)
    .OfClass(FamilyInstance)
    .ToElements()
@Mike.Buttery
I’m not sure where you’re going with checking for the existence of these three parameters, since beams already use only these three cover parameters… this can easily be confirmed by viewing the beam’s cover BuiltInParameters in the Properties tab or by inspecting them with Revit Lookup.
Furthermore, all structural beams in my project have the usage set to StructuralInstanceUsage.Girder. So, if I apply your code, it returns all beams in the project (as shown in the image below), which means the LogicalAndFilter would be redundant in this case.
I believe the issue lies elsewhere… possibly related to an incorrect definition or use of the curve_multiply_offset function within the main get_corrected_beam_length function.
For context, the curve_multiply_offset function is used to transform the extracted curve (the longest curve, which I call max_edge, obtained from the beam’s uncut solid geometry) into the top_curve and btm_curve, positioning them correctly according to the three cover parameters: top_cover, btm_cover, and side_cover.
Thanks.
One of your cover parameters is returning None so you have to exclude it (or deal with it)
Edit: Also look at possibility of using RebarHostData Class to access the cover information
@c.poupin
Effectively, I found the source of my problem… it occurs after temporarily reversing all beam junctions to obtain the full uncut beam solids, which I use to extract the max_edge in the main function get_corrected_beam_length…the issue originates from these lines inside that function:
def get_corrected_beam_length(beam, intersection_data, all_beams):
    for e in cut_elems:
    doc.Regenerate()
In this case, even though the Top and Bottom cover parameters are correctly updated and displayed in the Properties tab for all beams after calling the set_beam_covers function (and before reversing the beam junctions), the Other cover parameter loses its value once Revit regenerates the beam junctions. As a result, the Properties tab shows <multiples> for this parameter instead of the actual assigned value.
I tested the code below, which demonstrates this issue as shown in the following image.
import sys
import System
cover_faces = {
            return ct
    name = "Enrobage_{:.0f}cm".format(distance / 0.0328084)
    return new_ct
            if ct:
                param.Set(ct.Id)
    result = {}
                result[face] = ct.CoverDistance * 30.48
    return result
def get_solid(elem):
    opt = Options()
    opt.ComputeReferences = True
    opt.IncludeNonVisibleObjects = True
    geoSet = elem.get_Geometry(opt)
    for geo in geoSet:
        if isinstance(geo, Solid) and geo.Volume > 0:
            return geo
    for geo in geoSet:
        if isinstance(geo, GeometryInstance):
            geoSetInst = geo.GetInstanceGeometry()
            for geoI in geoSetInst:
                if isinstance(geoI, Solid) and geoI.Volume > 0:
                    return geoI
    return None
def get_beam_covers_after_cutting(beam):
    for e in cut_elems:
    doc.Regenerate()
    if not solid:
        return None
    return get_beam_covers(beam)
    .Where(System.Func[DB.Element, System.Boolean](lambda b: b.StructuralUsage == StructuralInstanceUsage.Girder))\
    .ToList()
    t.Start()
    for b in beams:
    t.Commit()
results_after_updating_cover = []
with Transaction(doc, "Compute Beam Rebar Curves") as t:
    t.Start()
    for beam in beams:
        results_after_updating_cover.append(get_beam_covers_after_cutting(beam))
    t.Commit()
OUT = results_after_updating_cover
How to adress this issue and properly reassign covers to beams after all junctions are regenerated?
Thanks.
@c.poupin
Please help me to solve this issue
Thanks.
I’ll try to look into it when I have a bit more time.
I’m not a structural engineer so I’m not making any promises.
can you try to useJoinGeometryUtils.SwitchJoinOrder before to set_beam_covers ?
I tried to set_beam_covers afeter JoinGeometryUtils.SwitchJoinOrder in the code below as you suggested where I got values for all covers keys as you can see in the output below, however some beams still displaying for missing values in the properties tab, and by inspecting that using Revit Lookup, I noticed that their property HasValue is False and their Element Id is non valid and set to -1
import sys
import System
cover_faces = {
            return ct
    return new_ct
            if ct:
                param.Set(ct.Id)
    result = {}
    return result
    opt = Options()
    for geo in geoSet:
            return geo
    for geo in geoSet:
                    return geoI
    return None
    for e in cut_elems:
    doc.Regenerate()
    if not solid:
        return None
    .ToList()
results_after_uncut = []
results_for_setting_covers = []
    t.Start()
    for beam in beams:
        set_beam_covers(beam, 10, 15, 8)
        results.append(get_beam_covers(beam))
    t.Commit()
OUT = results_after_uncut, results_for_setting_covers
Thanks.
one workaround to try is to use the get_corrected_beam_length function with JoinGeometryUtils.SwitchJoinOrder in a transaction with rollback.
an example with a decorator
import sys
import System
import functools
cover_faces = {
def decoTransaction(commit):
    def subDecoTransaction(func):
        @functools.wraps(func)
        def wrapper(*args, **kwargs):
            TransactionManager.Instance.ForceCloseTransaction()
            t = Transaction(doc, func.__name__)
            t.Start()
            ret = func(*args, **kwargs)
            if commit:
                t.Commit()
                t.RollBack()
            t.Dispose()
            return ret
        return wrapper
    return subDecoTransaction
    cover_types = FilteredElementCollector(doc).OfClass(RebarCoverType).ToElements()
            return ct
    return new_ct
@decoTransaction(commit = True)
            if ct:
                param.Set(ct.Id)
                print("test")
    result = {}
    return result
    opt = Options()
    for geo in geoSet:
            return geo
    for geo in geoSet:
                    return geoI
    return None
@decoTransaction(commit = False)
    for e in cut_elems:
    doc.Regenerate()
    if not solid:
        return None
    .ToList()
results = []
for beam in beams:
    print(beam.Id)
    results_for_setting_covers.append(get_beam_covers_after_cutting(beam))
Your workaround worked perfectly!.. by running the code below, I was able to update the cover parameters and compute both btm_curve and top_curve for each beam accordingly to these parameters as shown in the output below..this completely solved my issue.
beams network curves
import sys
import System
from System import Array
# ProtoGeometry
# Revit API
# Revit Nodes
# Revit Services
# System.Core
import functools
# Cover BuiltInParameter per beam faces
cover_faces = {
            t.Start()
            if commit:
                t.Commit()
                t.RollBack()
            t.Dispose()
            return ret
        return wrapper
# get or creat cover type
            return ct
    return new_ct
# subtransaction to set beam covers from user input
            if ct:
                param.Set(ct.Id)
                print("test")
# get updated beam covers
    result = {}
    return result
# get solid geometry from beams
    opt = Options()
    for geo in geoSet:
            return geo
    for geo in geoSet:
                    return geoI
    return None
# Get the side face normal where the max edge belongs
                return normal
    return None
    v1 = curve1.Direction.Normalize()
    v2 = curve2.Direction.Normalize()
    return v1.CrossProduct(v2).GetLength() <= tolerance
# Retrieve data from intersections between the current beam
# and beams connected at its start and end points
def get_intersecting_end_beams_data(single_beam, all_beams, tolerance=1e-3):
    """Returns intersection and cover info using RevitAPI curve intersections only."""
    top_cover = covers["Top"]
    btm_cover = covers["Bottom"]
    side_cover = covers["Other"]
    w_start = w_end = None
    start_side_cover = end_side_cover = None
    perpendicular_beams = []
            continue
        # Skip parallel
            continue
        # RevitAPI intersection
        results = clr.Reference[IntersectionResultArray]()
        result = loc_curve.Intersect(other_curve, results)
        if result != SetComparisonResult.Overlap:
            continue
        intersection_points = []
        interResult = results.Value
        intersection_points.append(interResult[0].XYZPoint)
        if not intersection_points:
            continue
        # Handle each intersection point
        for pt in intersection_points:
            perpendicular_beams.append(Element.Name.GetValue(beam.Symbol))
            other_covers = get_beam_covers(beam)
            other_side_cover = other_covers["Other"]
            # Check proximity to beam ends
            if start.DistanceTo(pt) < tolerance and w_start is None:
                w_start = b / 2
            elif end.DistanceTo(pt) < tolerance and w_end is None:
                w_end = b / 2
    beam_name = Element.Name.GetValue(single_beam.Symbol)
    print("Beam Type: {}".format(beam_name))
    print("  - Perpendicular beams:", perpendicular_beams)
    print("  - Start side cover in cm:", start_side_cover * 30.48)
    print("  - End side cover in cm:", end_side_cover * 30.48)
    print("-" * 50)
    return {
        "beam_width": w,
        "beam_height": h,
        "width_end": w_end,
# Transform created "btm_curve" and "top_curve" to their location according to cover parameters
def curve_multiply_offset(curve, vector, intersection_data):
    h = intersection_data["beam_height"]
    vertical_offset = h - (top_cover + btm_cover)
# main function to generate "btm_curve" and "top_curve" needed to create rebars.
    for e in cut_elems:
    doc.Regenerate()
    if not solid:
        return None
    # Pull intersection data
    start_side_cover = intersection_data["beam_start_side_cover"] or 0
    end_side_cover = intersection_data["beam_end_side_cover"] or 0
    # Identify main face and edge
        return None
        if max_edge_length <= 1e-9:
            return None
    # Generate top/bottom offset curves
    top_curve, btm_curve = curve_multiply_offset(new_line, face_normal, intersection_data)
# Collect beams
    .ToList()
btm_curves = []
top_curves = []
for beam in beams:
for beam in beams:
    intersection_data = get_intersecting_end_beams_data(beam, beams)
    result = get_corrected_beam_length(beam, intersection_data, beams)
    if not result:
        continue
    btm_curve, top_curve = result
Thanks a lot @c.poupin
Edited: can you suggest any improvements?
No, not particularly.
Since you’re working on this code, you could try making a version with PythonNet3 (Revit 2025+). That would be one less thing to do in the future.
I’m planning to install Revit 2025, and I’ll see how it goes with the use of PythonNet3.”
Thanks.