Spliting curves for creating beams rebars
Hi all, @c.poupin
In the code below, I am trying to create rebars for intersecting beams by splitting and overlapping each beam’s curve so that the Bar Length parameter of every rebar does not exceed 12.00 m, including hooks, for that I need to handle three main cases in the split_curve function, wher I defined three maximum straight segments to manage these scenarios:
  • case1 : total_length <= unit_length2
    • a single U-shaped rebar is generated
  • case2 : unit_length2 < total_length <= ref_length
    • two overlapped L-shaped rebar are generated where four sub-cases are considered:
      • sub_case1: total_length <= unit_length1: to avoid a single L-shaped rebar the main curve is shortened with a minimun distance eqaul to tol_near_full allowing the creation of a second overlapping L-shaped rebar
      • sub_case2: total_length == ref_length: Exactly two overlapping L-shaped rebars are generated, each with a length of 12.00 m.
      • sub_case3: ref_length - total_length <= tol_near_full: Similar to Sub-case 2, I force the creation of two overlapping L-shaped rebars, each 12.00 m long, this is achieved by extending the second rebar at its start point by a distance equal to tol_near_full and in this case the overlap length becomes lr + tol_near_full
      • sub_case4: ref_length - total_length > tol_near_full:two overlapping L-shaped rebar are generated where the straight segment for the first rebar is equal to unit_length1
  • case3: a list of multiples overlapping rebars are generated where:
    • At least one intermediate straight rebar of 12.00 m is created
    • The first rebar is L-shaped, with hook_90 at the start and None at the end.
    • The last rebar is L-shaped, with None at the start and hook_90 at the end.
    • the same rules in sub_case2 and sub_case3 are applied for the last bar in the list.
In the attached revit model below, I tested the code for the specific cases sub_case1 and sub_case2 where the results are as follow:
  • For both beams of type 400 x 800 along the X direction:
    • As expected, two overlapping L-shaped rebars (top and bottom) are generated, following the logic of Sub-case 1.
  • For both beams of type 300 x 600 along the Y direction:
    • Two overlapping L-shaped rebars are generated for the top rebars, following Sub-case 4.
    • No bottom rebar is generated, although I am handling Sub-case 2, where I expect exactly two overlapping L-shaped rebars, each 12.00 m long.
My question:
Could this issue be caused by floating-point imprecision when evaluating
total_length == ref_length, or is it more likely due to incorrect logic in my implementation?
beams_rebars
import sys
import System
import math
from System.Collections.Generic import IList, List
from System import Array
# ProtoGeometry
# Revit API
clr.AddReference('RevitAPI')
# Revit Nodes
# Revit Services
# System.Core
clr.AddReference("System.Core")
clr.ImportExtensions(System.Linq)
import functools
# collecting rebar type in the active document
rebar_types = (
    FilteredElementCollector(doc)
    .OfCategory(BuiltInCategory.OST_Rebar)
    .WhereElementIsElementType()
    .WherePasses(ElementClassFilter(RebarBarType))
    .ToElements()
top_bar_type = next((r for r in rebar_types if r.LookupParameter('Diamètre de barre').AsValueString() == "14 mm"), None)
btm_bar_type = next((r for r in rebar_types if r.LookupParameter('Diamètre de barre').AsValueString() == "16 mm"), None)
hook_types = list(FilteredElementCollector(doc).OfClass(RebarHookType).ToElements())
standard_hook_types = [hk for hk in hook_types if hk.Style == RebarStyle.Standard]
hook_90 = next((h for h in standard_hook_types if Element.Name.GetValue(h) == "Standard - 90 deg."), None)
# collecting beams cover BuiltInParameter
cover_faces = {
    "Top": BuiltInParameter.CLEAR_COVER_TOP,
    "Bottom": BuiltInParameter.CLEAR_COVER_BOTTOM,
    "Other": BuiltInParameter.CLEAR_COVER_OTHER
cover_types = list(FilteredElementCollector(doc).OfClass(RebarCoverType).ToElements())
def decoTransaction(commit):
    def subDecoTransaction(func):
        @functools.wraps(func)
        def wrapper(*args, **kwargs):
            TransactionManager.Instance.ForceCloseTransaction()
            t = Transaction(doc, func.__name__)
            t.Start()
            ret = func(*args, **kwargs)
            if commit:
                t.Commit()
                t.RollBack()
            t.Dispose()
            return ret
        return wrapper
    return subDecoTransaction
def get_cover_type(distance):
    for ct in cover_types:
        if abs(ct.CoverDistance - distance) < 1e-6:
            return ct
    name = "Enrobage_{:.0f}cm".format(distance / 0.0328084)
    new_ct = RebarCoverType.Create(doc, name, distance)
    cover_types.append(new_ct)
    return new_ct
@decoTransaction(commit = True)
def set_beam_covers(beam, top, btm, side):
    cover_cm = {"Top": top, "Bottom": btm, "Other": side}
    cover_ft = {face: cover_cm[face] * 0.0328084 for face in cover_cm}
    for face, bip in cover_faces.items():
        param = beam.get_Parameter(bip)
        if param and param.StorageType == StorageType.ElementId:
            ct = get_cover_type(cover_ft[face])
            if ct:
                param.Set(ct.Id)
                print("test")
def get_beam_covers(beam):
    result = {}
            ct = doc.GetElement(param.AsElementId())
            if isinstance(ct, RebarCoverType):
                result[face] = ct.CoverDistance
    return result
# getting beams solid geometry
def get_solid(elem):
    opt = Options()
    opt.ComputeReferences = True
    opt.IncludeNonVisibleObjects = True
    geoSet = elem.get_Geometry(opt)
    for geo in geoSet:
        if isinstance(geo, Solid) and geo.Volume > 0:
            return geo
    for geo in geoSet:
        if isinstance(geo, GeometryInstance):
            geoSetInst = geo.GetInstanceGeometry()
            for geoI in geoSetInst:
                if isinstance(geoI, Solid) and geoI.Volume > 0:
                    return geoI
    return None
#Retrieving the beam’s side face to extract its longest curve.
def get_side_face_normal(solid, edge):
    for face in solid.Faces:
        if edge in [e for loop in face.EdgeLoops for e in loop]:
            normal = face.FaceNormal
            if not (normal.IsAlmostEqualTo(XYZ.BasisZ) or normal.IsAlmostEqualTo(-XYZ.BasisZ)):
                return normal
    return None
def is_curves_parallel(curve1, curve2, tolerance=1e-6):
    v1 = curve1.Direction.Normalize()
    v2 = curve2.Direction.Normalize()
    return v1.CrossProduct(v2).GetLength() <= tolerance
# Retrieving data from the ends of each intersected beam to generate the main rebar curve.
def get_intersecting_end_beams_data(single_beam, all_beams, tolerance=1e-3):
    loc_curve = single_beam.Location.Curve
    w = single_beam.Symbol.LookupParameter("b").AsDouble()
    h = single_beam.Symbol.LookupParameter("h").AsDouble()
    covers = get_beam_covers(single_beam)
    top_cover = covers["Top"]
    btm_cover = covers["Bottom"]
    side_cover = covers["Other"]
    start = loc_curve.GetEndPoint(0)
    end = loc_curve.GetEndPoint(1)
    w_start = w_end = None
    start_side_cover = end_side_cover = None
    perpendicular_beams = []
    for beam in all_beams:
        if beam.Id == single_beam.Id:
            continue
        other_curve = beam.Location.Curve
        # Skip parallel
        if is_curves_parallel(loc_curve, other_curve):
            continue
        results = clr.Reference[IntersectionResultArray]()
        result = loc_curve.Intersect(other_curve, results)
        if result != SetComparisonResult.Overlap:
            continue
        intersection_points = []
        interResult = results.Value
        intersection_points.append(interResult[0].XYZPoint)
        if not intersection_points:
            continue
        # Handle each intersection point
        for pt in intersection_points:
            b = beam.Symbol.LookupParameter("b").AsDouble()
            other_covers = get_beam_covers(beam)
            other_side_cover = other_covers["Other"]
            if start.DistanceTo(pt) < tolerance and w_start is None:
                w_start = b / 2
                start_side_cover = other_side_cover
            elif end.DistanceTo(pt) < tolerance and w_end is None:
                w_end = b / 2
                end_side_cover = other_side_cover
    return {
        "beam_width": w,
        "beam_height": h,
        "beam_top_cover": top_cover,
        "beam_btm_cover": btm_cover,
        "beam_side_cover": side_cover,
        "width_start": w_start,
        "width_end": w_end,
        "beam_start_side_cover": start_side_cover,
        "beam_end_side_cover": end_side_cover
# transform function to create top and bottom rebar curve for each beam
def curve_multiply_offset(curve, vector, intersection_data):
    h = intersection_data["beam_height"]
    top_cover = intersection_data["beam_top_cover"]
    btm_cover = intersection_data["beam_btm_cover"]
    side_cover = intersection_data["beam_side_cover"]
    curve = curve.CreateTransformed(Transform.CreateTranslation(XYZ(0, 0, -1).Multiply(top_cover)))
    vertical_offset = h - (top_cover + btm_cover)
    trans = Transform.CreateTranslation(vector.Negate().Multiply(side_cover))
    top_curve = curve.CreateTransformed(trans)
    bottom_trans = Transform.CreateTranslation(XYZ(0, 0, -1).Multiply(vertical_offset))
    btm_curve = top_curve.CreateTransformed(bottom_trans)
    btm_curve = Line.CreateBound(btm_curve.GetEndPoint(1), btm_curve.GetEndPoint(0))
    return top_curve, btm_curve
@decoTransaction(commit = False)
def get_corrected_beam_length(beam, intersection_data, all_beams):
    beam_curve = beam.Location.Curve
    direction = beam_curve.Direction
    beam_length = beam_curve.Length
    start = beam_curve.GetEndPoint(0)
    cut_elems = [doc.GetElement(xId) for xId in SolidSolidCutUtils.GetCuttingSolids(beam)]
    for e in cut_elems:
        JoinGeometryUtils.SwitchJoinOrder(doc, beam, e)
    doc.Regenerate()
    solid = get_solid(beam)
    if not solid:
        return None
    beam_width = intersection_data["beam_width"]
    beam_height = intersection_data["beam_height"]
    w_start = intersection_data["width_start"] or 0
    w_end = intersection_data["width_end"] or 0
    start_side_cover = intersection_data["beam_start_side_cover"] or 0
    end_side_cover = intersection_data["beam_end_side_cover"] or 0
    # Identify main face and edge
    max_edge = max(solid.Edges, key=lambda x: x.ApproximateLength)
    max_edge_curve = max_edge.AsCurve()
    max_edge_direction = max_edge_curve.Direction
    max_edge_length = max_edge_curve.Length
    face_normal = get_side_face_normal(solid, max_edge)
    if face_normal is None:
        return None
    if max_edge_length > beam_length:
        if not max_edge_curve.GetEndPoint(0).Z == beam_curve.GetEndPoint(0).Z:
            max_edge_curve = Line.CreateBound(
                XYZ(max_edge_curve.GetEndPoint(0).X, max_edge_curve.GetEndPoint(0).Y, beam_curve.GetEndPoint(0).Z),
                XYZ(max_edge_curve.GetEndPoint(1).X, max_edge_curve.GetEndPoint(1).Y, beam_curve.GetEndPoint(1).Z)
        if not max_edge_direction.IsAlmostEqualTo(direction):
            max_edge_curve = Line.CreateBound(max_edge_curve.GetEndPoint(1), max_edge_curve.GetEndPoint(0))
        if max_edge_length <= 1e-9:
            return None
        new_start = max_edge_curve.Evaluate(start_side_cover / max_edge_length, True)
        new_end = max_edge_curve.Evaluate(1 - (end_side_cover / max_edge_length), True)
        new_line = Line.CreateBound(new_start, new_end)
        total_length = beam_length + w_start + w_end - (start_side_cover + end_side_cover)
        project_point = start + face_normal.Multiply(beam_width / 2)
        new_start = project_point - direction.Multiply(w_start - start_side_cover)
        new_end = new_start + direction.Multiply(total_length)
    # Generate top/bottom offset curves
    top_curve, btm_curve = curve_multiply_offset(new_line, face_normal, intersection_data)
    return top_curve, btm_curve, face_normal
# splitting top/bottom curve for each beam
def split_curve(curve, bar_type, hook_type):
    # the main curve length
    total_length = curve.Length
    print(total_length * 0.3048)
    # bar diameter
    d = bar_type.BarModelDiameter
    # standard hook Bend Diameter
    D = bar_type.StandardHookBendDiameter
    # hook extension length
    l = hook_type.GetHookExtensionLength(bar_type)
    # hook total length
    b = l + D / 2 + d
    # referance length to generate a staright bar without hooks.
    unit_length = 12 / 0.3048
    # referance length to generate an L-shapped rebar.
    unit_length1 = (12 / 0.3048) - b - ((D + d) * math.pi / 4) + D + 2 * d
    # referance length to generate an U-shapped rebar.
    unit_length2 = (12 / 0.3048) - 2 * b - ((D + d) * math.pi / 2) + 2 * D + 4 * d
    # overlap distance
    lr = 50 * d
    # tolerence distance needed to forcing creation of an L-shapped rebar with 12.00m long
    tol_near_full = 0.15 / 0.3048
    # referance length to exactely generate two overlaped L-shapped rebar with 12.00m long
    ref_length = 2 * unit_length1 - lr
    print(ref_length * 0.3048)
    direction = curve.Direction
    curves = []
    start = curve.GetEndPoint(0)
    end = curve.GetEndPoint(1)
    k = 0
    n = int((total_length-unit_length1-lr) // unit_length)
    # Case 1: a single U-shaped rebar is generated
    if total_length <= unit_length2:
        curves.append(curve)
    # Case 2: Two overlapped L-shaped rebars are generated
    elif unit_length2 < total_length <= ref_length:
        if total_length <= unit_length1:
            end1 = start + direction.Multiply(total_length - tol_near_full)
            start2 = end1 - direction.Multiply(lr)
            new_line1 = Line.CreateBound(start, end1)
            new_line2 = Line.CreateBound(start2, end)
            curves.append(new_line1)
            curves.append(new_line2)
            if ref_length - total_length <= 1e-3:
                end1 = start + direction.Multiply(unit_length1)
            elif ref_length - total_length <= tol_near_full:
                start2 = end1 - direction.Multiply(lr + tol_near_full)
    return curves
# Collect beams
beams = FilteredElementCollector(doc)\
    .OfCategory(BuiltInCategory.OST_StructuralFraming)\
    .WhereElementIsNotElementType()\
    .Where(System.Func[DB.Element, System.Boolean](lambda b: b.StructuralUsage == StructuralInstanceUsage.Girder))\
    .ToList()
btm_curves = []
top_curves = []
normal_vects = []
for beam in beams:
    set_beam_covers(beam, 3, 3, 5)
for beam in beams:
    intersection_data = get_intersecting_end_beams_data(beam, beams)
    result = get_corrected_beam_length(beam, intersection_data, beams)
    if not result:
        continue
    top_curve, btm_curve, normal_vect = result
    top_curves.append(split_curve(top_curve, top_bar_type, hook_90))
    btm_curves.append(split_curve(btm_curve, btm_bar_type, hook_90))
    normal_vects.append(normal_vect)
# function to create rebars
def create_rebars_from_segments(beam, top_sublist, btm_sublist, normal_vect, top_bar_type, btm_bar_type, hook_type,n):
    rebars = []
    rebars_length = []
    direction = beam.Location.Curve.Direction
    width = beam.Symbol.LookupParameter("b").AsDouble()
    first_top = top_sublist[0]
    if normal_vect.CrossProduct(direction).IsAlmostEqualTo(XYZ(0, 0, -1)):
        norm  = first_top.Direction.CrossProduct(XYZ.BasisZ)
        hook_orient = RebarHookOrientation.Right
        norm = first_top.Direction.CrossProduct(XYZ.BasisZ).Negate()
        hook_orient = RebarHookOrientation.Left
    l1 = len(top_sublist)
    l2 = len(btm_sublist)
    for idx,top in enumerate(top_sublist):
        if l1 <= 2:
            if l1 ==1:
                start_hook = hook_type
                end_hook = hook_type
                if idx == 0:
                    end_hook = None
                    start_hook = None
            if idx == 0:
                end_hook = None
            elif idx == l1 - 1:
                start_hook = None
                start_hook = None
                end_hook = None
        # --- create top rebar ---
        top_list = List[Curve]()
        top_list.Add(top)
        top_rebar = Rebar.CreateFromCurves(
            doc,
            RebarStyle.Standard,
            top_bar_type,
            start_hook,
            end_hook,
            beam,
            norm,
            top_list,
            hook_orient,
            hook_orient,
            True, True
        top_rebar.GetShapeDrivenAccessor().SetLayoutAsFixedNumber(
            n, width - 2 * side_cover, True, True, True
        rebars.append(top_rebar)
        rebars_length.append(top_rebar.get_Parameter(BuiltInParameter.REBAR_ELEM_LENGTH).AsDouble() * 304.8)
    for idx,btm in enumerate(btm_sublist):
        if l2 <= 2:
            if l2 ==1:
                if idx == 0:
                    end_hook = None
                    start_hook = None
            if idx == 0:
                end_hook = None
            elif idx == l2 - 1:
                start_hook = None
                start_hook = None
                end_hook = None
        # --- create bottom rebar ---
        btm_list = List[Curve]()
        btm_list.Add(btm)
        btm_rebar = Rebar.CreateFromCurves(
            doc,
            btm_bar_type,
            start_hook,
            end_hook,
            beam,
            norm,
            btm_list,
            hook_orient,
            hook_orient,
            True, True
        btm_rebar.GetShapeDrivenAccessor().SetLayoutAsFixedNumber(
        rebars.append(btm_rebar)
        rebars_length.append(btm_rebar.get_Parameter(BuiltInParameter.REBAR_ELEM_LENGTH).AsDouble() * 304.8)
    return rebars, rebars_length
all_beam_rebars = []
all_beam_rebars_length = []
with Transaction(doc, "Create Beam Rebars from Segments") as t:
    t.Start()
    for beam, top_curves_list, btm_curves_list, normal_vect in zip(beams, top_curves, btm_curves, normal_vects):
        beam_rebars, rebars_length = create_rebars_from_segments(
            beam, top_curves_list, btm_curves_list, normal_vect,
            top_bar_type, btm_bar_type, hook_90, 3
        all_beam_rebars.extend(beam_rebars)
        all_beam_rebars_length.extend(rebars_length)
    t.Commit()
OUT = all_beam_rebars, all_beam_rebars_length, [c.ToProtoType() for lst in top_curves for c in lst], [c.ToProtoType() for lst in btm_curves for c in lst]
beams_rebar_test4.rvt (3.6 MB)
Any help would be appreciated
Thanks.
Hey,
It looks like you have a lot of progress and you are nearly there! Great work!
I find that if I am getting unexpected results, I need to focus on commenting my code so I am clear on exactly what everything is doing.
I try to output variable values throughout the code, at places where I need to make sure that everything is working as expected, to ensure that I am getting the correct results.
If the code is too long or unmageable, I might even split it down into different python nodes, and then I can move on with confidence.
Once the code is working as I expect, I will go back and modularise it, add in functions, classes etc. to make it run more smoothly. I find it quite hard to debug while building with lots of functions.
It can be laborious to make all the processes, but ultimately if it gets your code working, it was worth it!
I hope that helps,
Mark
Yes. You should ALWAYS round before doing a comparison after any type of unit or source comparison, and as you’re using Python you are converting from the C# Revit API (which itself is a conversion from true native Revit) to Python in Dynamo. Otherwise it isn’t a question of IF floating point math will burn you, but rather WHEN floating point math will burn you.
Hi @Mark.Ackerley
First of all, have you had a chance to test the code to see how it behaves, and could you suggest a possible solution?
Do you think my explanation of the different parts of the code was not clear enough?
I agree with you…the code was indeed too long, so I had to split it into different Python nodes to make it more readable and to isolate the section where I’m encountering the issue, which should help with debugging.
Thanks.
Hi @jacob.small
In the split_curve function I replaced this line
By this line
if round(ref_length - total_length, 3) <= 1e-3:
However I end up with the same issue!
Thanks.
Might not have been impacting this case directly, but always best practice to round before comparing.
Sadly I’m on a phone and we’re looking at… Well it’s more lines of code then I can count in this UI. It might be best to write each of these ‘cases’ as a single function, test those one by one on a particular beam to make sure the inner workings are set up right, and then build the if statement logic gates but have them just log which case would be used to an output.
By pulling the parts pulled out into modules you can test individual components instead of limiting it to the output alone.
@c.poupin @Mike.Buttery
My issue is resolved for cases 1 and 2, however as you can see in the image below, I’m struggling to handle the case3 when remaining_length falls within the following range:
unit_length1 - lr < remaining_length < unit_length - lr
In this situation even though the last segment is an L-shaped bar with the correct length, the second-to-last bar ends up with an extra 12.00m length. This is incorrect because the bar end is pushed beyond the beam. Therefore, this segment should be shortened by a distance equal to:
excess = unit_length - (lr + remaining_length)
Here is a simplified version of the code for beam rebars, focusing on the curve-splitting logic:
import sys
import System
import math
# ProtoGeometry
# Revit API
# Revit Nodes
# Revit Services
# System.Core
import functools
# collecting rebar types in the current document
rebar_types = (
    .ToElements()
# getting rebar bartype with diameter "16mm"
bar_type = next((r for r in rebar_types if r.get_Parameter(BuiltInParameter.REBAR_BAR_DIAMETER).AsValueString() == "16 mm"), None)
# collecting RebarHookType in the current document
# filtering RebarHookType by RebarStyle "Standard"
# getting RebarHookType "Standard - 90 deg."
# beam cover BuiltInParameter by face
cover_faces = {
# check for existing or creating a new RebarCoverType
            return ct
    return new_ct
# set beam RebarCoverType from user input
            if ct:
                param.Set(ct.Id)
                print("test")
# collect curent beam RebarCoverType
    result = {}
    return result
# split curve function to create multiple overlapping rebars
def split_curve(beam, bar_type, hook_type):
    start_pt = curve.GetEndPoint(0).Add(direction.Multiply(side_cover))
    end_pt = curve.GetEndPoint(1).Add(direction.Negate().Multiply(side_cover))
    rebar_curve = Line.CreateBound(start_pt, end_pt)
    # the main curve to split
    total_length = rebar_curve.Length
    # Hook Length
    b = l + D / 2 + d
    # Hook Tangent Length
    a = b + ((D + d) * math.pi / 4) - D - 2 * d
    print(b * 0.3048)
    print(a *0.3048)
    # maximum straight  length segment to generate a straight rebar with Bar length = 12.00 m
    # maximum straight  length segment to generate an L-shaped rebar with Bar length = 12.00 m
    unit_length1 = unit_length - b - ((D + d) * math.pi / 4) + D + 2 * d
    # maximum straight  length segment to generate an U-shaped rebar with Bar length = 12.00 m
    unit_length2 = unit_length - 2 * b - ((D + d) * math.pi / 2) + 2 * D + 4 * d
    # overlapping distance
    lr = 50 * d
    # tolerance distance used for extending or shortening Bar Length
    # maximum lenght for generating exactely two overlapping L-shaped rebars
    curves = []
    start = rebar_curve.GetEndPoint(0)
    end = rebar_curve.GetEndPoint(1)
    k = 0
    # Case 1: Single U-shaped rebar
    if round(total_length, 3) == round(unit_length2, 3):
        curves.append(rebar_curve)
    # Case 2: Two overlapping L-shaped rebars
    elif round(unit_length2, 3) < round(total_length, 3) <= round(ref_length, 3):
        if round(total_length, 3) <= round(unit_length1, 3):
            if round(ref_length, 3) == round(total_length, 3):
            elif round(ref_length - total_length, 3) <= round(tol_near_full, 3):
                start2 = end - direction.Multiply(unit_length1)
    # Case 3: Multiple overlapping rebars
        end1 = start.Add(direction.Multiply(unit_length1))
        start2 = new_line1.GetEndPoint(0).Add(direction.Multiply(unit_length1 - lr))
        while k < n+1:
            end2 = start2.Add(direction.Multiply(unit_length))
            new_line2 = Line.CreateBound(start2, end2)
            k += 1
            next_start = start2.Add(direction.Multiply(unit_length - lr))
            remaining_length = rebar_curve.GetEndPoint(1).DistanceTo(end2)
            print(remaining_length*0.3048)
            if round(remaining_length, 3) <= round(unit_length1 - lr, 3):
                remaining_curve = Line.CreateBound(next_start, rebar_curve.GetEndPoint(1))
                curves.append(remaining_curve)
                break
            start2 = next_start
    return curves
# function to create multiple overlapping rebars from splited curves
def create_rebars_from_segments(beam, curves_list, bar_type, hook_type,n):
    rebars = []
    normal_vect = XYZ(0,-1,0)
        norm  = direction.CrossProduct(XYZ.BasisZ)
        norm = direction.CrossProduct(XYZ.BasisZ).Negate()
    # Rebar Shape Generated Based on curves_list Length "l" (U-Shaped, L-Shaped, or Straight)
    l = len(curves_list)
    # if l = 1 : a single U-Shaped rebar is generated (hooks at both ends)
    # if l = 2 : two overlapping L-shaped rebars are generated
    # if l >= 3 : multiple overlapping rebars with  where:
    # first rebar is an L-shaped
    # at least one intermediate straight rebar of 12.00 m
    # last rebar is an L-shaped
    for idx,crv in enumerate(curves_list):
        # determinating hook position based on the generated shape
        if l <= 2:
            if l ==1: # single segment: U-shaped (hooks at both ends)
            else:  # two segments: two overlapping L-shaped rebars
                if idx == 0:
                    end_hook = None
                    start_hook = None
        else:  # multiple segments:
            if idx == 0:
                end_hook = None
            elif idx == l - 1:
                start_hook = None
                start_hook = None
                end_hook = None
        # create rebars
        rebar_list = List[Curve]()
        rebar_list.Add(crv)
            doc,
            bar_type,
            start_hook,
            end_hook,
            beam,
            norm,
            rebar_list,
            hook_orient,
            hook_orient,
            True, True
        rebars.append(rebar)
    return rebars
# Collect girder beams only
    .ToList()
# Set default covers (cm)
with Transaction(doc, "set beam cover") as t:
    t.Start()
    for b in beams:
        set_beam_covers(b, 3, 3, 5)
    t.Commit()
rebar_curves = []
rebars = []
    t.Start()
    for b in beams:
        rebar_crv = split_curve(b, bar_type, hook_90)
        rebar = create_rebars_from_segments(b, rebar_crv, bar_type, hook_90,3)
        rebar_curves.append(rebar_crv)
    t.Commit()
OUT = [c.ToProtoType() for lst in rebar_curves for c in lst]
Please check my used Revit model below
beam_rebars_test.rvt (2.5 MB)
Thanks.
I was finally able to solve my issue…the trick was to detect the overflow distance by computing the cumulative_length during each iteration within the while loop. Once the overflow is detected, it means that an extra 12.00 m segment has been generated beyound the beam, which needs to be shortened at its endpoint by the excess distance.
here the final code:
import sys
import System
import math
# ProtoGeometry
# Revit API
# Revit Nodes
# Revit Services
# System.Core
import functools
rebar_types = (
    .ToElements()
cover_faces = {
            return ct
    return new_ct
            if ct:
                param.Set(ct.Id)
                print("test")
    result = {}
    return result
    # Hook Length
    b = l + D / 2 + d
    #print(b * 0.3048)
    #print((b + ((D + d) * math.pi / 4) - D - 2 * d)*0.3048)
    lr = 50 * d
    curves = []
    k = 0
        start2 = start.Add(direction.Multiply(unit_length1 - lr))
        cumulative_length = unit_length1
        lengths = []
        while k < n+1:
            is_full_length = False
            cumulative_length += (unit_length - lr)
            lengths.append(cumulative_length * 0.3048)
            if round(cumulative_length - total_length, 3 ) >= 0:
                is_full_length = True
                excess = cumulative_length - total_length + d + D/2
                end2 = start2.Add(direction.Multiply(unit_length - excess))
                end2 = end2
            k += 1
            if remaining_length <= unit_length1-lr:
                if is_full_length == True:
                    next_start = next_start.Add(direction.Negate().Multiply(excess))
                break
            start2 = next_start
    print(beam.Id)
    print([l for l in lengths])
    print("_" * 25)
    return curves
    rebars = []
        if l <= 2:
                if idx == 0:
                    end_hook = None
                    start_hook = None
            if idx == 0:
                end_hook = None
            elif idx == l - 1:
                start_hook = None
                start_hook = None
                end_hook = None
        # create rebars
        rebar_list.Add(crv)
            doc,
            bar_type,
            start_hook,
            end_hook,
            beam,
            norm,
            rebar_list,
            hook_orient,
            hook_orient,
            True, True
    return rebars
    .ToList()
    t.Start()
    for b in beams:
    t.Commit()
rebar_curves = []
rebars = []
    t.Start()
    for b in beams:
    t.Commit()
Thanks.